Path Segment Error (Invalid Tag Name)

(1/1)

gusterminator:
I created a new routine.  I added a JSR on Main page to link to the new routine.  Everything works In the new routine....program wise.  I then added a new Form to Advanced HMI.  I added the EitherNetIP communication driver.  When ever I link something from my new Form I get this error "Path Segment Error (Invalid Tag Name)"  I have checked spelling......copy paste exact name.....nothing works from the new routine on my new form page.  If I link to something from the Main routine from the new Form it works.

any ideas what might be causing this???

Thanks,

dmroeder:
Maybe your tag was created as a "Program Scope" tag rather than a "Controller Scope"?

If it is program scoped, it can still be read, you just have to change the format a bit:

PROGRAM:ProgramName.TagName

You would have to replace "ProgramName" with the name of the program that the tag was created in and replace "TagName" with the name of your tag.

timryder:
What PLC. This very much matters.

HillMakeItBetter:

--- Quote from: dmroeder on November 13, 2017, 07:42:26 PM ---PROGRAM:ProgramName.TagName

You would have to replace "ProgramName" with the name of the program that the tag was created in and replace "TagName" with the name of your tag.

--- End quote ---

I did not read between the lines, but figured it out.  Only replace "ProgramName" and replace "TagName" as noted.  Leave the word PROGRAM: (or Program:) as is.

Here is an example that worked for me connecting to AB PLC:
"Program:RFID_Controllers.RFID_Max_Read[0]"

Maybe this example will help someone else, or me - sometime later.

Phrog30:
This link will have some useful info to the next person as well.
https://advancedhmi.com/documentation/index.php?title=EthernetIPforCLXCom