Author Topic: NumericSevenSegment - polling and Analog Output  (Read 997 times)

Darrell

  • Full Member
  • ***
  • Posts: 198
  • Electrician / PLC Technician
    • View Profile
NumericSevenSegment - polling and Analog Output
« on: December 05, 2014, 09:36:56 PM »
Using a NumericSevenSegment I try reading the the value from analog output such as O:2.2 but will always get the the value from the first input O:2.0

Darrell

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5270
    • View Profile
    • AdvancedHMI
Re: NumericSevenSegment - polling and Analog Output
« Reply #1 on: December 06, 2014, 08:38:35 PM »
There is a known issue with directly reading IO on a SLC/MicroLogix. The work around is to move the value to an integer and use the integer value in the HMI.