I was messing around with a Compactlogix processor, and I found that if I try to read a Program tag, I get an error.
Invalid Tag Address. CIP Status4
Controller tags work fine.
My solution is to Copy the Program tag array in the PLC over to a controller tag array.
I then referenced the controller tag because I know that works.
AdvancedHMIv35'
Is there something else that I could have done in order to read Program tags?
-
To access program scope tags use the following format:
PROGRAM:ProgramName.TagName
-
I tried MainProgram.MyArray[94], but no luck.
What would I use to read the value of 7812 (MyArray[94])?
maybe you can tell from the photo?
-
Try it like this:
PROGRAM:MainProgram.MyArray[94]
-
That did it
I think I had a space in there somewhere
Thanks a lot!