General Category => Open Discussion => Topic started by: RajSHJ on December 19, 2018, 06:09:54 AM

Title: Reading and displaying Real formats
Post by: RajSHJ on December 19, 2018, 06:09:54 AM
I am getting real values in a database from a siemens S7 1200 PLC which is configured as as Modbus TCP server. Each value occupies 2 modbus registers. When I choose register 40001for example I am getting a displayed value which is far beyond the actual. Can you help me configure it properly? I set number of element as 2.
Title: Re: Reading and displaying Real formats
Post by: Archie on December 19, 2018, 07:00:02 AM
You need to use what is referred to as address modifers:

F40001

or 40001@F in the latest beta version


https://www.advancedhmi.com/forum/index.php?topic=765.0