General Category => Support Questions => Topic started by: mourazo on November 18, 2019, 04:17:55 PM

Title: Read Modbus RTU 16bits
Post by: mourazo on November 18, 2019, 04:17:55 PM
I am trying to read data from a device that transmits in modbus RTU 16 bit, without existing, I obtaining a baud rate exception  when the parameter is correct, i can't read with easyModbus library, I obtain a parse int error but i can read with modbus poll program.  What is the correct way to read it?
Title: Re: Read Modbus RTU 16bits
Post by: Godra on November 18, 2019, 06:05:33 PM
In AHMI, the correct way to read it is to add ModbusRTUCom driver to the form, set COM port parameters correctly, add a BasicLabel to the form and input a PLC register address in the PLCAddressValue field. Run the program and see what that BasicLabel will show.
Title: Re: Read Modbus RTU 16bits
Post by: mourazo on November 19, 2019, 02:15:03 AM
When I execute I obtain a baudrate exception, different when I execute with a modbus 32 bits equipments, i cant find The correct configuration in a modbusRTUcom driver. Thanks
Title: Re: Read Modbus RTU 16bits
Post by: Godra on November 19, 2019, 02:40:26 AM
You need to provide far more details like what is the model of the device you are using, what COM port parameters are you using and any other info.
Title: Re: Read Modbus RTU 16bits
Post by: Godra on November 19, 2019, 04:52:08 PM
As a test, see if you can connect to your device with Modbus Master app from this post:

https://www.advancedhmi.com/forum/index.php?topic=765.msg15223#new
Title: Re: Read Modbus RTU 16bits
Post by: mourazo on December 03, 2019, 12:05:40 PM
thank you, it´s solved, it was a problem of the equipment