General Category => Support Questions => Topic started by: PJonHar on February 18, 2020, 11:36:42 AM
-
Hi,
Version:3.99y Beta 34
I have the following program that subscribes to tags via code (ignore the IPAddress).
private EthernetIPforCLXCom PLCComms = null;
private List<int> SubscriptionIDs = new List<int>();
public K_AutoExternal AEX { get; set; } = new K_AutoExternal();
private string AEXParentTag = "Robot1";
public MainWindow()
{
InitializeComponent();
DataContext = this;
PLCComms = new EthernetIPforCLXCom();
PLCComms.BeginInit();
PLCComms.IniFileName = "CLX.ini";
PLCComms.IniFileSection = "PLCComms";
PLCComms.EndInit();
PLCComms.ComError += this.PLCComms_ComError;
SubscribeAEXTags();
PLCComms.ReadClock();
}
private void UnsubscribeAEXTags()
{
foreach (int i in SubscriptionIDs)
PLCComms.Unsubscribe(i);
SubscriptionIDs.Clear();
}
private void SubscribeAEXTags()
{
try
{
UnsubscribeAEXTags();
PropertyInfo[] properties = typeof(K_AutoExternal).GetProperties();
foreach (PropertyInfo property in properties)
SubscriptionIDs.Add(PLCComms.Subscribe(String.Format("{0}.{1}", AEXParentTag, property.Name), 1, 5000, SubscriptionCallback));
}
catch (Exception ex)
{
MessageBox.Show(ex.Message, ex.TargetSite.Name);
}
}
private void SubscriptionCallback(object sender, PlcComEventArgs e)
{
if (e.ErrorId == 0 && e.Values != null && e.Values.Count > 0)
ParseData(e.PlcAddress, e.Values[0]);
}
private void ParseData(string tag, string value)
{
try
{
PropertyInfo[] properties = typeof(K_AutoExternal).GetProperties();
foreach (PropertyInfo property in properties)
{
if (String.Format("{0}.{1}", AEXParentTag, property.Name) == tag)
{
TypeConverter typeConverter = TypeDescriptor.GetConverter(AEX.GetType().GetProperty(property.Name).PropertyType);
object propValue = typeConverter.ConvertFromString(value);
AEX.GetType().GetProperty(property.Name).SetValue(AEX, propValue, null);
AEX.UpdateProperties();
break;
}
}
}
catch (Exception ex)
{
MessageBox.Show(ex.Message, ex.TargetSite.Name);
}
}
private void PLCComms_ComError(object sender, PlcComEventArgs e)
{
Console.WriteLine(e.ErrorId + " - " + e.ErrorMessage);
}
The tags get updated, but only on the initial execution of the program.
The following error messages appear at each poll:
0 - EIPTransport.SendData-No Response
-22 - No Response from PLC(22)
The pollrate is quite high (5000ms), so i think this is okay.
Any ideas what it could be?
-
In your other post you asked about a BeginInit and EndInit.
You should try adding those to the section where you set the properties of the EthernetIPforCLXCom driver.
See this also: https://www.advancedhmi.com/forum/index.php?topic=2207.msg12718#msg12718
-
Please see revised post.
The Callback works now, but again only for the initial program execution.
I still get the same errors messages after the first subscription.
-
As a test, use fresh AdvancedHMI solution and, instead of the code, use existing components and visual controls to try to communicate with your PLC.
-
I have used the original project and added a BarLevel looking directly at a tag in the PLC, and this communicates fine.
So, what am i doing wrong with the Subscribing?
-
Put breakpoints at these lines and see what values are in those blue variables:
* foreach (PropertyInfo property in properties)
* SubscriptionIDs.Add(PLCComms.Subscribe(String.Format("{0}.{1}", AEXParentTag, property.Name), 1, 5000, SubscriptionCallback));
Also put a breakpoint in the callback to see if it stops there:
* if (e.ErrorId == 0 && e.Values != null && e.Values.Count > 0)
-
Hi,
Checked all the variables in the Class and they exist as tags within the PLC.
Please see console output:
------------ Start Application ------------
Finished Subscribing.
------------ Frist Callback ------------
Robot1.AUT - False
Robot1.AlarmStopExternal - True
Robot1.AlarmStopInternal - True
Robot1.ApplicationRunning - False
Robot1.Calibrated - True
Robot1.CommandDWord0 - 1073741874
Robot1.CommandDWord1 - 0
Robot1.ConfirmMessage - False
Robot1.ControllerReady - True
Robot1.CouldStartMotion - True
Robot1.CycleStart - True
Robot1.DriveEnable - True
Robot1.DrivesOff - True
Robot1.DrivesOn - False
Robot1.EXT - True
Robot1.EnableIn - True
Robot1.EnableOut - True
Robot1.ExternalStart - False
Robot1.FaultReset - False
Robot1.HeartBeat - False
Robot1.HeartBeatFault - True
Robot1.HeartBeatReflect - False
Robot1.Home - True
Robot1.Home1 - False
Robot1.Home2 - False
Robot1.Home3 - False
Robot1.Home4 - False
Robot1.Home5 - False
Robot1.IOActive - True
Robot1.IOActiveConfirmation - True
Robot1.MoveEnable - True
Robot1.NearPositionReturn - True
Robot1.OnPath - True
Robot1.ParityMode - 0
Robot1.PeriReady - True
Robot1.ProgramActive - True
Robot1.ProgramMoving - False
Robot1.ProgramNumber - 0
Robot1.ProgramNumberReflect - 0
Robot1.ProgramNumberRequest - True
Robot1.ProgramNumberValid - False
Robot1.QuickStop - False
Robot1.RobotReadyInternal - True
Robot1.SPSRunning - True
Robot1.StatusDWord0 - 1658783608
Robot1.StatusDWord1 - 0
Robot1.StopMessage - False
Robot1.Stopped - True
Robot1.T1 - False
Robot1.T2 - False
Robot1.UserSafety - True
Robot1.WaitingDriveEnable - False
Robot1.WaitingErrorAcknowledge - False
Robot1.WaitingExternalStart - False
Robot1.WaitingProgramNumber - True
Robot1.WaitingProgramNumberEcho - False
------------ Second Callback ------------
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
SubscriptionCallback - -22 - No Reponse from PLC 10.44.16.192, slot=0
PLC_ComError - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
SubscriptionCallback - -22 - No Response from PLC(22)
PLC_ComError - 0 - EIPTransport.SendData-No Response
-
You cannot be stuck with this issue, just try a different approach like to comment out your subscription line of code and add a new line where you directly subscribe to a tag or two.
Or try adding and using the DataReceived event of the driver while setting the callback to null:
PLCComms.Subscribe(String.Format("{0}.{1}", AEXParentTag, property.Name), 1, 5000, null)
-
Since when subscribing your own code become a support issue with AAHMI?
Have a little self respect and post it in the 'Open' forum.
-
It could also be that your poll rate is too high and the driver is timing out.
Try setting the poll rate to 250 and/or set the driver's Timeout to a higher value than the poll rate.
-
You cannot be stuck with this issue, just try a different approach like to comment out your subscription line of code and add a new line where you directly subscribe to a tag or two.
Or try adding and using the DataReceived event of the driver while setting the callback to null:
PLCComms.Subscribe(String.Format("{0}.{1}", AEXParentTag, property.Name), 1, 5000, null)
Tried this and i got the attached error.
It could also be that your poll rate is too high and the driver is timing out.
Try setting the poll rate to 250 and/or set the driver's Timeout to a higher value than the poll rate.
I tried this and I got the same errors as before.
I have found that if i only subscribe to 15 tags, the callback works fine?
private void SubscribeAEXTags()
{
try
{
UnsubscribeAEXTags();
int _subscribeTotal = 15;
int _subscribeCount = 0;
PropertyInfo[] properties = typeof(K_AutoExternal).GetProperties();
foreach (PropertyInfo property in properties)
{
if (_subscribeCount < _subscribeTotal)
{
Console.WriteLine(String.Format("{0}.{1}", AEXParentTag, property.Name));
SubscriptionIDs.Add(PLC.Subscribe(String.Format("{0}.{1}", AEXParentTag, property.Name), 1, 250, null));
_subscribeCount++;
}
}
Console.WriteLine("Finished Subscribing.");
}
catch (Exception ex)
{
MessageBox.Show(ex.Message, ex.TargetSite.Name);
}
}
Since when subscribing your own code become a support issue with AAHMI?
Have a little self respect and post it in the 'Open' forum.
Everything okay over there?? This is a support question as the subscribe isn't working.
-
Maybe try using multiple instances of the DataSubscriber2 component.
Make sure to read all the posts in this topic:
https://www.advancedhmi.com/forum/index.php?topic=2451.0
-
I have tested subscribing to the raw data (i.e. the IO data) and this successfully subscribes and calls back 32 bits.
private void SubscribeTestTags()
{
try
{
string _testTage = "Robot1:I.Data[0]";
int _subscribeTotal = 32;
int _subscribeCount = 0;
UnsubscribeTags();
for (int i = 0; i < _subscribeTotal; i++)
{
string tag = String.Format("{0}.{1}", _testTage, i.ToString());
Console.WriteLine(tag);
SubscriptionIDs.Add(PLC.Subscribe(tag, 1, 250, SubscriptionTestCallback));
}
_subscribeCount++;
Console.WriteLine("Finished Subscribing.");
}
catch (Exception ex)
{
MessageBox.Show(ex.Message, ex.TargetSite.Name);
}
}
So, I tried subscribing only to the properties of type bool, however i still get the same original errors.
If i change it to subscribe to only 15 bool properties, it worked again.
-
Just keep trying.
You can still consider using multiple DataSubscriber2 components.
-
Is there a way to enable logging on the comms driver?
-
Why not just create a function which reads the tag data directly from the PLC and stores their values in your own variable?
REALLY rough example, i write VB.net mostly.
try
{
//Create a new Driver instance
var plcDriver = new AdvancedHMIDrivers.EthernetIPforCLXCom();
plcDriver.IPAddress = "192.168.1.1";
plcDriver.PollRateOverride = 150;
string _testTage = "Robot1:I.Data[0]";
int _subscribeTotal = 32;
int _subscribeCount = 0;
//UnsubscribeTags();
for (int i = 0; i < _subscribeTotal; i++)
{
string tag = String.Format("{0}.{1}", _testTage, i.ToString());
Console.WriteLine(tag);
string _testTagData = plcDriver.Read(tag);
Console.WriteLine(_testTagData);
someDataContainer.Add(_testTagData);
}
_subscribeCount++;
Console.WriteLine("Finished Subscribing.");
}
catch (Exception ex)
{
MessageBox.Show(ex.Message, ex.TargetSite.Name);
}
-
I already have a work around for the unknown issue with my subscription method.
I have a timer based on a given timespan that uses the same code.
private void tagTimer_Tick(object sender, EventArgs e)
{
string tag;
PropertyInfo[] properties = typeof(K_AutoExternal).GetProperties();
foreach (PropertyInfo property in properties)
{
tag = String.Format("{0}.{1}", AEXParentTag, property.Name);
ParseData(tag, PLC.Read(tag));
}
}
I would still like to try and identify why my subscription does not work.
-
Is there a way to enable logging on the comms driver?
Regarding the above, does anyone know?
-
There is some info here:
https://www.advancedhmi.com/forum/index.php?topic=2636.0
-
Beta 35 may possibly fix this
-
Beta 35 may possibly fix this
I have just tested Beta 36, and i can confirm this is now working (i.e. the subscriptions are working as expected).
Thanks.