General Category => Support Questions => Topic started by: frenelius on March 31, 2021, 02:13:49 AM
-
Hello,
I am testing HMI to see if I can replace the NB displays, but I cannot get to have full communication with the PLC through OmronEthernetFINSCom.
PLC CJ2M-CPU31
In some cases, I can write to D0, but will not get a valid response back from the PLC. And I have not been able to read D0 never.
Attached the Wireshark capture. PLC address is 10.0.0.1, AHMI is 10.0.0.5.
Do anybody know if it is just a configuration problem?
I have been trying different options (TargetNetworkAddress, TargetNodeAddress, Private, Public...) without luck.
Thanks a lot!
-
According to the error code being received 0x0502
"Relaying is not possible because there are no routing tables"
-
But the error I see in Wireshark is 0x8502, is it the same as 0x0502?
Thanks.
-
The 8 indicates a network relay error
-
Attached is more specific information