General Category => Support Questions => Topic started by: Integram01 on April 25, 2022, 07:50:14 AM
-
Hi,
I am new to using Advanced HMi and recently i am playing around with it. I am trying to use tags that are addressed indirectly in my PLC, and when i am using the indirectly addressed tag in the tag connection it gives me runtime error "invalid tag name", is there a way to use indirectly addressed tags? please advise.
-
Are you trying to post to the alt.read.my.mind?
I am not as good as Archie's mind reader capability.
Tell us PLC type, what is tag looks like?
-
If you have an array that you are addressing there are 2 ways . 1st in the plc copy the result of the indirect address to a new tag and send that . 2nd copy the array to the hmi using the data subscriber and also the index and use VB to get the indirect tag . can't say more without plc type and more detail on what you want to achieve .