General Category => Support Questions => Topic started by: ronj on October 05, 2015, 08:45:57 PM
-
Hi,
I have a LinearMeterV set to display 0-100.0% from a PLC value that is 0-1000 (value scale factor = 0.1). This works fine.
The target value from the PLC is scaled the same way, however the target value display isn't scaled when it is displayed. It doesn't seem to be influenced by the value scale factor.
Is there some way to scale the target value, either the same as the value or independently?
Regards,
Ron
-
Hmmm... never ran across this before. If you are using version 3.99, I made a quick patch that will get around this:
https://sourceforge.net/projects/advancedhmi/files/advancedhmi/3.5/Patches
Download and unzip MfgControl.AdvancedHMI.ControlsPatchV399a.zip
Replace the file in AdvancedHMIControls\Support
Rebuild the solution
This gives a new property of ScaleTargetValue which will be set to True by default.
The tolerances do not scale, so you will have to adjust them accordingly.
If you are not using version 3.99, then your best option may be to create a scaled value in the PLC
-
Thanks for the quick fix. Problem solved (I am running 3.99a).
Just so you know... the new property appears to have a typo ScaleTargetVale (u missing).
I also ran into another problem with this control when a comms error (using ModbusTCP) caused an error in CDbl(). My fix in LinearMeterVert.vb starting at line line 42 is this:
If ValueScaleFactor = 1 Then
MyBase.Text = value
Else
'in case value contains a comms error message - cannot convert to Dbl
Try
MyBase.Text = CDbl(value) * ValueScaleFactor
Catch ex As Exception
MyBase.Text = value
End Try
End If
I think these two issues (target scaling and issue with a comms error) also apply to the horizontal version LinearMeterH. I haven't tried this one as much as the vertical version.
Regards,
Ron
-
Thanks for the feedback. I put a fix in for that one.