Support Questions / Re: How to make push button work with Micrologix 1200?
« on: March 02, 2016, 10:32:43 AM »
I tested all the different OutputType with the BasicButton, none works.
This section allows you to view all posts made by this member. Note that you can only see posts made in areas you currently have access to.
Put B3/0 in PLCAddressClick
Add a BasicLabel and set the PLCAddressValue to N7:0 in order to verify your communications. If everything is communicating, the BasicLabel will change to a number.
I just did a quick test using DF1Com with a MicroLogix 1100 and using version 3.99d. I tested with both AUTO baud and setting the correct baud rate, which was 19200.
I simply added a BasicLabel and set PLCAddressValue to N7:0
In both cases it worked correctly for me.
Hello buddy did u figure it out
Am using DF1 and I did turn the rslinx off still not working ? Any luck