Support Questions / Re: clx driver wont write to tags on a particular pc
« on: September 10, 2019, 08:09:45 PM »
Hi Archie, turns out that the plc tag being a timer accumulator was being written as a zero by the timer reset function at the same time we were trying to write to it. It just happened to be at the same time we were testing this particular pc.
So there was absolutely nothing wrong with the pc at all. Sorry for wasting your time.

2
Support Questions / Re: clx driver wont write to tags on a particular pc
« on: September 10, 2019, 01:08:29 AM »
Ok will do. Thanks

3
Support Questions / clx driver wont write to tags on a particular pc
« on: September 09, 2019, 06:02:50 PM »
Hi Archie, we are using the clx driver to read and write tags. On a particular pc on windows 7 we can read but not write to tags. No exceptions are flagged. The same program is running on other pc's with windows 7 without issues.
Could there be a pc setting that would stop this write function?   

4
Thanks Archie, we ended up removing the NATR unit and set up a few VPN tunnels to achieve the same outcome. Thanks for your time.

5
Hi, I cannot establish a plc connection through a Allen Bradley 1783-NATR unit. Not sure if it is possible.
iam using the clxdriver we purchased and it works fine with a connection outside of this device.
The network translation device is needed because we have a private plc network and are giving our IT network access to a few plc values through this device. Thanks. 
 