Support Questions / Re: Only reading 1 array register
« on: May 15, 2024, 11:08:37 AM »
Yes, this is the second time for an issue like this. First was a ControlLogix V32. I was not able to read several registers from an outside network and the HMI stopped reading from the PLC. A download "fixed" that. Rockwell recommended a firmware update, which I did. Have not seen that one again.
Second is the one posted here, which I have already described.
This recent one with the 5380 is version 32.12.
I updated the ControlLogix L83ES to version 32.16.
Yes, at least some of the data was in a UDT.
I am in a production environment. Luckily, it has only been informational data affected, machine performance, HMI display. So didn't stop anything from running. Other than the time to troubleshoot and fix...
Second is the one posted here, which I have already described.
This recent one with the 5380 is version 32.12.
I updated the ControlLogix L83ES to version 32.16.
Yes, at least some of the data was in a UDT.
I am in a production environment. Luckily, it has only been informational data affected, machine performance, HMI display. So didn't stop anything from running. Other than the time to troubleshoot and fix...