I found a small bug in version 3.9.9.24 of the EthernetIPforSLCMicroCom that didn't exist in 3.9.9.20. I mapped the output bits of a MicroLogix 1400 PLC to a BasicIndicator. It worked fine for the internal outputs (O:0/x), or the expansion module outputs (O:1/x), but not if both existed in the same form. When they were in the same form the indicators for the expansion module would all simultaneously flash.
My solution was to put a bit coil in parallel with the output coil on the PLC and map the bits in AdvancedHMI.