Author Topic: Advanced HMI with Micrologix 1400  (Read 2302 times)

CarlosGranados

  • Newbie
  • *
  • Posts: 5
    • View Profile
Advanced HMI with Micrologix 1400
« on: January 19, 2018, 06:31:31 PM »
Hi Everyone, i want to create an interface between a Micrologix1400 and AdvancedHmi v3.99X
i have a problem with it.
 following the instructions 1)-6) in order to link rslogix500 and AdvancedHmi
Im unsig the ip on plc 192.168.0.10
on ethernetIPforCLXCom1 is the same
im using on my computer 192.168.0.xxx, can link good the plc and the pc.
so, im using a digitalpanelmeter with PLCAddressValue N7:0
when i start the program with VS15, but its appears the message "Path destination unknow"
can some one please can tellme, whats going on?
thank you su much for your attention.

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: Advanced HMI with Micrologix 1400
« Reply #1 on: January 19, 2018, 07:02:15 PM »
You need to use the EthernetIPforSLCMicroCom

dmroeder

  • Administrator
  • Full Member
  • *****
  • Posts: 212
    • View Profile
Re: Advanced HMI with Micrologix 1400
« Reply #2 on: January 19, 2018, 09:00:06 PM »
Just to add a bit, the EthernetIPforCLXCom driver is for CompactLogix and ControlLogix.  The EthernetIPforSLCMicroCom driver is for SLC and Micrologix, like your Micrologix 1400.

CarlosGranados

  • Newbie
  • *
  • Posts: 5
    • View Profile
Re: Advanced HMI with Micrologix 1400
« Reply #3 on: January 20, 2018, 09:33:12 AM »
Its Works Fine, Thank you a lot :)

« Last Edit: January 20, 2018, 09:54:12 AM by CarlosGranados »