Author Topic: Send que full, may have lost connection or data request too fast  (Read 1643 times)

amotomura

  • Newbie
  • *
  • Posts: 3
    • View Profile
I have a project that is displaying around 40 Dints on the Main Form using 40 AdvancedHMI.BasicLabels.

I've used this project on other PLC's, but on this particular one, I get an error : Send que full, may have lost connection or data request too fast

It sometimes works, but more often than not errors.

I found this link for a solution, but I'm not sure where to insert the recommended code:

http://advancedhmi.com/forum/index.php?topic=194.msg625#msg625

Thanks,
Andrew




Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: Send que full, may have lost connection or data request too fast
« Reply #1 on: April 14, 2014, 01:05:45 PM »
This problem comes typically from a slow communication rate, a very busy Ethernet network, or one with a lot of errors. If you have a managed switch, you can check the error rate to see if there is possibly a bad cable.

You can also reduce the poll rate by changing to PollRateOverride property of the driver. Try setting it to 500 or even 1000.