RSLinx Classic OEM Node Connection
« on: September 05, 2019, 10:56:42 AM »
Good Morning,

I currently am able to pull information from our SLC 5/03 in AdvancedHMI. I am only able to do this from node 1 (see attached screenshot of RSLinx Classic OEM)

However, whenever I try to pull information from the SLC with node 11 I am unsuccessful in my attempt.

These are both showing up on my RSLinx DH+ network and I am getting communication from node 11 looking at the data monitor.

Is there something that I am missing when configuring pulling data from another node?

Any and all information would be greatly appreciated

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: RSLinx Classic OEM Node Connection
« Reply #1 on: September 05, 2019, 11:44:16 AM »
What version of AdvancedHMI?

Is it safe to assume you are going through a KF2 module?

PoppaDollz

  • Newbie
  • *
  • Posts: 7
    • View Profile
Re: RSLinx Classic OEM Node Connection
« Reply #2 on: September 05, 2019, 01:18:26 PM »
I'm seeing "AdvancedHMIV35"

And yes you are correct I have configured a KF2 module

We are using an Equustek DL4500 module and we have previously logged data of all nodes through excel successfully with the attached driver configuration

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: RSLinx Classic OEM Node Connection
« Reply #3 on: September 05, 2019, 01:59:07 PM »
Can you set EnableLogging to True, then run the application with the address that does not work. Then post the log file that is created in the bin\Debug directory

PoppaDollz

  • Newbie
  • *
  • Posts: 7
    • View Profile
Re: RSLinx Classic OEM Node Connection
« Reply #4 on: September 05, 2019, 02:36:11 PM »
See Attached:

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: RSLinx Classic OEM Node Connection
« Reply #5 on: September 05, 2019, 04:04:33 PM »
Based on the last packets:

14:34:24.9474001 Send   : 10 02 0B 35 0F 00 53 41 A2 06 05 87 0B 00 10 03 DE
14:34:24.9524001 Rcvd   : 10 06
14:34:24.9734001 Rcvd   : 10 02 35 0B 4F 07 53 41 10 03 D6
 

An STS code is returned of value 07

According to the DF1 Manual:

07 Station is offline


Does both C5:11 and C5:12 exist in the PLC?

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: RSLinx Classic OEM Node Connection
« Reply #6 on: September 05, 2019, 04:05:57 PM »
I seem to remember DH+ is octal addressing, but AdvancedHMI nodes are decimal. Try node 9 in AdvancedHMI

PoppaDollz

  • Newbie
  • *
  • Posts: 7
    • View Profile
Re: RSLinx Classic OEM Node Connection
« Reply #7 on: September 05, 2019, 04:29:13 PM »
Archie,

DH+ is Octal I did not realize that AHMI was decimal

After switching the target node to 9 it worked!

Thank you very much for your help!

bachphi

  • Hero Member
  • *****
  • Posts: 671
    • View Profile
Re: RSLinx Classic OEM Node Connection
« Reply #8 on: September 05, 2019, 05:29:00 PM »
What is the connection between PC & DL4500? is it Ethernet patch cable with RJ45 connector?
===================================================
This is NOT alt.read.my.mind.
No such thing is sh^t-for-brains unless you are posting to alt.read.my.mind.
===================================================