Author Topic: AutomationDirect Proto X remote I\O adapter  (Read 2074 times)

larryhts

  • Jr. Member
  • **
  • Posts: 98
    • View Profile
AutomationDirect Proto X remote I\O adapter
« on: September 20, 2019, 07:11:46 AM »
Has anyone tried to use the Modbus TCP driver with an AutomationDirect Proto X remote I\O adapter? I have used them with a P-2 550 PLC from AutomationDirect. I will be trying from an AdvancedHMI PanelPC. Hoping to be able to cut down on equipment needed for small projects in our test lab. Like running some test equipment with just a Panel PC and remote I\O ( no PLC )

https://cdn.automationdirect.com/static/manuals/pxuserm/pxuserm.html

bachphi

  • Hero Member
  • *****
  • Posts: 690
    • View Profile
Re: AutomationDirect Proto X remote I\O adapter
« Reply #1 on: September 20, 2019, 01:06:26 PM »
I am not sure if this is possible, but it is with Ethernet/IP.
Price wise I am not so sure either.

PX-TCP1 Bus coupler       $253
PX-148   8-point 24VDC IN   $57
PX-248   8-point 24VDC OUT   $66


1734-AENT         $521
1734-IV8            $116
1734-OV8E         $189

Software superior :  Rockwell win    $10,000
UCL =================
This is NOT alt.read.my.mind.
No such thing is sh^t-for-brains unless you are posting to alt.read.my.mind.
My understanding of computer is well below six Σ.
Unless what I am saying is logically defined in a PLC, everything else might be beyond my control.
LCL =================

larryhts

  • Jr. Member
  • **
  • Posts: 98
    • View Profile
Re: AutomationDirect Proto X remote I\O adapter
« Reply #2 on: September 20, 2019, 02:28:39 PM »
Bachphi

I have the Px order coming next week and will set up to try them with AHMI. I’ll post the results.
Thanks

larryhts

  • Jr. Member
  • **
  • Posts: 98
    • View Profile
Re: AutomationDirect Proto X remote I\O adapter
« Reply #3 on: September 25, 2019, 06:30:36 AM »


I received the Protos X components yesterday and used the Free software for configuring them to set the IP. The software scans and gives you the modbus addresses for all the I/O you have connected.  It works great and is very inexpensive.

PX-TCP1 Bus coupler               $253
PX-148   8-point 24VDC IN           $57
PX-248   8-point 24VDC OUT   $66
PX-901       Terminal End Cap         $13.50