Author Topic: multiple com bridges  (Read 5919 times)

Joe Matkowski

  • Newbie
  • *
  • Posts: 47
    • View Profile
multiple com bridges
« on: October 22, 2019, 01:58:52 PM »
I am having to move about 128 tags from an automation direct plc to our contrologix platform any suggestions on an efficient way to do this?

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5360
    • View Profile
    • AdvancedHMI
Re: multiple com bridges
« Reply #1 on: October 22, 2019, 02:13:14 PM »
Which AutomationDirect PLC? Does it support Ethernet/IP? I would use direct PLC to PLC if possible.

Joe Matkowski

  • Newbie
  • *
  • Posts: 47
    • View Profile
Re: multiple com bridges
« Reply #2 on: October 22, 2019, 02:20:14 PM »
DL-06 with ethernet only supports modbus tcp that I am aware of and do not want to put a prosoft modbus module in our rack.. I have the modbus side working just trying to be efficient with comms

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5360
    • View Profile
    • AdvancedHMI
Re: multiple com bridges
« Reply #3 on: October 22, 2019, 03:46:48 PM »
I only use the ComBridge as a last resort because of potential issues such as someone closing the app or turning off the PC.

The ComBridge uses the normal subscription mechanism, so it goes into the pool of being optimized for you.

Joe Matkowski

  • Newbie
  • *
  • Posts: 47
    • View Profile
Re: multiple com bridges
« Reply #4 on: October 23, 2019, 09:43:39 AM »
Thanks for the help I'm really out of ideas on this project.

-jdm 


Joe Matkowski

  • Newbie
  • *
  • Posts: 47
    • View Profile
Re: multiple com bridges
« Reply #6 on: October 29, 2019, 01:43:21 PM »
Thanks everyone I figured out I could use the C-more panel on the skid will do the translations.   

-jdm