I tried that with no luck. I've matched the IP to the ENI, and I get a "Write Failed!No response from PLC during write" error.
The ENI module should work, but there is a bug in the firmware. If a connection is not properly closed, the ENI module will not release it. Eventually it will tie up all connections. If possible cycle the power on the module and try again. Be sure to use the EthernetIPforSLCMicro driver.
Cycled power, still same thing. Write error failure. I'm using the EthernetIPforSLCMicro driver.
I'm probably just going to bite the bullet and spend the money to buy a 5/05 processor to get this ball rolling, unless you have another idea. We didn't want to do that because we are planning on doing a full controls overhaul in the coming future, which will be Beckhoff processor, ect.