Author Topic: Modbus TCP  (Read 1307 times)

MrPike

  • Sr. Member
  • ****
  • Posts: 297
    • View Profile
Modbus TCP
« on: December 06, 2014, 11:25:27 PM »
I am using AHMI3.87 to communicate to two seperate controllers via modbus TCP. One controller I am communicating just fine, it is connected via 2wire serial to a serial-ethernet(multinet FE) converter at 9600bps. The other is connected via 4 wire serial-ethernet(lantronics) converter at 19.2kbps.  The later one will not communicate with AHMI and gives me a msg box that reads "No response from PLC(21)" and the basic label values display "CommFail--20".  I am able to use Modscan32 without any issues and can read data just fine.  I went ahead and used modsim and AHMI communicates just fine with it. I did previously communicate to the later when I was connected via 2 wire but had too many comm fail messages that I converted back thinking the lantronics converter preferred a 4 wire config.  Is the serial configuration an issue, does AHMI care? Thanks   

Archie

  • Administrator
  • Hero Member
  • *****
  • Posts: 5322
    • View Profile
    • AdvancedHMI
Re: Modbus TCP
« Reply #1 on: December 07, 2014, 08:36:42 AM »
I did confirm this to be a problem with the driver. I was able to fix it for the next release of 3.88, which should be posted by tonight.